GerryB
Senior Member
- Location
- woodbridge, ct. USA
Well, this is a new one for me. I don't fail many inspections, but this one wasn't supposed to be inspected. This is the same job I posted about a breaker tripped the day after I was there and I went back and it was totally unrelated to any work I did. So because of that the HO called her friend, supposedly a retired AHJ and he looked or she probably asked him to look at the work I did. So there was a 4" octagon box in the basement, I pulled out 2 bx and entered 3 romex, 12-2. So yes the box has 9 wires counting the ground instead of 6, and 2 open holes where I pulled out the bx. He (retired guy) told her there was to many wires in the box and the open holes were a fire hazard. Any thoughts? I changed the box. There is no permit on the job as this GC does a lot of kitchens and baths and doesn't normally pull permits. This job wasn't even a gut job.