synchro
Senior Member
- Location
- Chicago, IL
- Occupation
- EE
I agree with that since it's a separately derived system, as Carultch has also mentioned.Not that this is necessarily wrong synchro, but more specifically, the wye point should be grounded and bonded per 250.30(A), specifically look at (A)(4)