Exterior Receptacles for Restaurant Patio

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
210 part III has all the general required outlets, majority of the requirements are in 210.52 which applies to dwellings and 210.60 that applies to guest rooms/suites/dormitories or similar.

Hardly anything else is required for receptacle outlets in the remainder of requirements except a receptacle to service HVAC equipment and a receptacle near the service equipment.
 

curious101

Senior Member
Location
Atlanta, GA, USA
210 part III has all the general required outlets, majority of the requirements are in 210.52 which applies to dwellings and 210.60 that applies to guest rooms/suites/dormitories or similar.

Hardly anything else is required for receptacle outlets in the remainder of requirements except a receptacle to service HVAC equipment and a receptacle near the service equipment.

Thank you!
 

tom baker

First Chief Moderator
Staff member
Just a note on the difference in load calcs for dwelling and non dwelling.
Dwelling units have a long list of required receptacle locations, but even with 100 receptacles on a circuit, they are included in 3 VA per Sq Ft calculation.
But non dwelling units every receptacle installed counts as 180 VA. As pointed out, a service area receptacle is required, HVAC equipment, and for a conference room. Other than that no receptacles are required, but most users find them handy
 