Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
When swapping out panels I often find the GEC terminated more than five feet from the entrance to the basement. Running a new GEC can be a problem with finished basements. What is the least expensive option available to be set up to extend a GEC #4 awg?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The least expensive irreversible splice is a crimp connector but it would require some type of tool to compress it. What do you mean about the 5' is that the connection to the water pipe electrode?
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
Yes, that is the situation. The existing GEC falls short of the five foot requirement. In older houses the GEC was terminated to an accessible water pipe near the panel.
The 5 ft requirement is only when the water pipe qualifies as a GEC. If it’s a bonding connection it can be made anywhere
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, that is the situation. The existing GEC falls short of the five foot requirement. In older houses the GEC was terminated to an accessible water pipe near the panel.
Just out of curiosity where's the water meter in this scenario? It seem strange that an older home would not have the GEC landed on the street side of the water meter which is around here is right where the pipe enters the house.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Can the new grounding electrode conductor be run on the outside of the house and then enter back where the water line enters the house.
 