Expansion joints

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
I live in the mid west, how far can i run 1 1/2" aluminum conduit on roof of a building with out a expansion joint ?
 
Last edited by a moderator:

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
In the 2020NEC handbook, the informational note on 300.7 suggests to multiple the values in table 352.44 by 0.40 for aluminum conduit. 352.44 tells you when you might need an expansion joint but you'd have to do more work to know what your environmental conditions.
 

tom baker

First Chief Moderator
Staff member
You need to know the max and min temps to calculate the Delta T. Then with the length you cakculate the expansion. Get the delta T from the national weather service for your area
 