Equipment Grounding Conductor

Status
Not open for further replies.

danilo

Member
Guys,

is it safe to use the minimum 8mm2 TW wire as equipment grounding for 70A,MCCB if the bus symmetrical fault current calculation is 18ka?

appreciate your comment

Thanks

Danilo
 

coulter

Senior Member
Re: Equipment Grounding Conductor

Originally posted by danilo:
...is it safe to use the minimum 8mm2 TW wire as equipment grounding for 70A,MCCB ...
If you are working to the NEC, table 250.122 gives the required sizes.

Originally posted by danilo:
...equipment grounding for 70A,MCCB if the bus symmetrical fault current calculation is 18ka?...
I've not ever seen where the available fault current effects the size of an equipment grounding conductor.

carl
 

celtic

Senior Member
Location
NJ
Re: Equipment Grounding Conductor

Originally posted by coulter:
What's an "MCCB"?

carl
molded case circuit breaker (MCCB)
P3a-mccb.jpg
 

danilo

Member
Re: Equipment Grounding Conductor

yeah i guess it will when a L-G,L-L-G occured in the system..actually,its an unsymmetrical fault..just worried if 8mm2 could withstand the 18ka.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: Equipment Grounding Conductor

The available short circuit current does not affect the ground wire size.

8 mm^2 metric size wire is about #8.

Table 250.122 says that #8 can be used on a circuit with an OCPD of not more than 100A.

However, I am not sure if 8mm^2 wire is just a hair smaller than #8 or just a hair larger. If it is larger than #8, you would be OK (assuming you have not increased the size of your power conductors). If in fact 8mm^2 wire is just a hair smaller than #8, than you would have to use the chart selection for the next size down (#10) which is only good for a 60A OCPD.

<added> I did a little more searching. It appears 8mm^2 wire is slightly smaller than #8, so I would conclude it is too small to use as the egc on a circuit supplied by a 70A OCPD.

[ August 01, 2005, 08:17 AM: Message edited by: petersonra ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Equipment Grounding Conductor

Bob,
The available short circuit current does not affect the ground wire size.
Actually it does. Look at 250.4(A)(5) and the note at the bottom of Table 250.122.
Don
 

rcwilson

Senior Member
Location
Redmond, WA
Re: Equipment Grounding Conductor

Per the IEEE Buff Book, Fig 150, (1986 edition) #8 awg can handle 18000 A for 0.01 seconds (less than a cycle) before the insulated copper conductor reaches 200C and melts the insulation beyond repair.

If the fault current is really 18,000 A, a #4 AWG (25 mm) would be needed to keep the temperature below 200C. Assumptions: MCB clearing time of .02 seconds, initial temperature 75C, final temperature 200 C, rubber insulation.

A smaller wire may not fuse and melt at these ampacities, but it could get hot enough to do damage to the power wiring in the same raceway.

Note that it only takes 20 feet of #8 wire to reduce the maximum fault current below the wires' 9000 A short circuit rating, assuming the same MCB clearing time.
 

danilo

Member
Re: Equipment Grounding Conductor

Originally posted by rcwilson:

If the fault current is really 18,000 A, a #4 AWG (25 mm) would be needed to keep the temperature below 200C. Assumptions: MCB clearing time of .02 seconds, initial temperature 75C, final temperature 200 C, rubber insulation.

yeah i must agree with this analysis coz in my opinion, the values in Table 250.122 might have been computed differently or a higher rating of short circuit fault might not have considered.,just imagine if a 100A,MCCB will use #8 for its EGC connected to a bus with 22ka..could it be that this #8 is way below the minimum already?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: Equipment Grounding Conductor

Originally posted by rcwilson:
...#8 awg can handle 18000 A for 0.01 seconds (less than a cycle) before the insulated copper conductor reaches 200C and melts the insulation beyond repair.
Wow! And I thought my Weller soldering gun got hot quickly!
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: Equipment Grounding Conductor

Originally posted by don_resqcapt19:
Bob,
The available short circuit current does not affect the ground wire size.
Actually it does. Look at 250.4(A)(5) and the note at the bottom of Table 250.122.
Don
Why don't they write these things in an understandable way?

I suppose it must be time to buy a new handbook. My 1990 copy does not even have a paragraph 250.4.
 