Equipment grounding conductor size

hhsting

Senior Member
So I have heat pump MCA 17.2A and MOCP of 25A.

Phase and neutral provided is sized per MCA #12 AWG.

Breaker provided is sized 25A per MOCP.

Question minimum equipment grounding conductor size should it be #12 AWG or #10 AWG?
 

augie47

Moderator
Staff member
Location
Tennessee
Do you happen to look at a Code book ?

250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122,
but in no case shall they be required to be larger than the circuit conductors supplying the equipment
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
250.122 Size of Equipment Grounding Conductors.
(A) General. Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122,
but in no case shall they be required to be larger than the circuit conductors supplying the equipment
'Ceptin' the parallel feeder installation. ;)
 