slo7682

Member
The NEC doesn't seem to differentiate the minimum size of the equipment grounding conductor run with feeder conductors for LV systems, say 600V and below, vs. medium and high voltage systems, say 5 KV and 15KV. Is the proper size for medium and high voltage systems based on 250.122?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Equipment Grounding Conductor Run with 5KV or 15KV Feede

The code does not really address higher voltage systems, but remember that Table 250.122 is the minimum permitted size of the EGC and that 250.4 may require the use of a larger conductor.
Don
 

rcwilson

Senior Member
Location
Redmond, WA
Re: Equipment Grounding Conductor Run with 5KV or 15KV Feede

See the thread "melted ground wire" for some discussion on this. NEC required EGC wire size is a minimum. That size should be verified against the expected fault current and the fault clearing time and the cable's short time withstand curve.

Several guides and cable suppliers' websites have these curves. (IEEE Brown Book, Okonite Technical Manual, Southwire Power Cable Manual)

Note that the numbers quoted in the other post refer to the fusing limit of bare ground conductors which is around 1000C temperature. We really want to keep the copper temperature under 250C during a fault to prevent insulation damage.
 