Equipment Grounding Conductor Bonded to Metal Enclosure

Status
Not open for further replies.

Gategator37

Senior Member
All,

08' NEC 250.148(C) requires a connection from the equipment grounding conductor to a metal enclosure. I have a #1/0 egc being spliced in an enclosure, the electrician has tapped off of this #1/0 ground with a #8 and bonded the #8 to the enclosure. From what I have learned in the past, you always bond to the enclosure with the largest egc that is spliced in the enclosure, and since we only have one egc (#1/0) then that would be the minimum size that can be used.

I am having problems finding the code reference that specifically states this... Or is 250.148(C) the only reference I have?

As always I appreciate your help.
 

jumper

Senior Member
250.102(D) Size — Equipment Bonding Jumper on Load Side
of an Overcurrent Device.
The equipment bonding jumper
on the load side of an overcurrent device(s) shall be sized
in accordance with 250.122.
 