Hi all, so I have this one massive Single Family project where the home is 3600 sq ft in LA County. Demand Amps were originally 173A, so we were going with a 200A service and a panel with a 200A bus rating. Solar (which is required for new Construction in CA) was allocated 9.6kW of continuous load while using the 120% rule. I recently received the following plan check comment:
For all new one and two-family dwelling units, the service panels and/or sub-panels shall have the capacity of an additional load not less than 5kVA for every 2,000 square feet of living space, designated to accommodate future energy storage system(s). This load shall be considered continuous and demand factors shall not apply. Additionally, the service panels and/or sub-panels shall have space(s) reserved/dedicated to permit installation of the branch circuit overcurrent protective device(s) for energy storage system. (LACEC 220.41).
It looks like LA county Incorporated requirements on having Energy Storage Systems (ESS) earlier than the state and the counties that I mostly complete projects in, which are on NEC 2017. With this new ESS demand at 125% this bumps my service size to 400A with a demand of 225A (10kW added). I updated the Bus ratings to 400A with a 225A main breaker.
My question is, with the main breaker being 225A and the bus rating being 400A, does this comply with NEC2017 705.12(B)(2)(3)(a) which would allow for the PV and ESS to be located on separate circuits, anywhere on the panel? I'd place them on the very last circuits on the panel, but I'm curious about others' thoughts.
If it doesn't comply, I would definitely appreciate feedback on other ways one may go about adding the "future" ESS loads to the system while still complying with NEC requirements. Thanks!
For all new one and two-family dwelling units, the service panels and/or sub-panels shall have the capacity of an additional load not less than 5kVA for every 2,000 square feet of living space, designated to accommodate future energy storage system(s). This load shall be considered continuous and demand factors shall not apply. Additionally, the service panels and/or sub-panels shall have space(s) reserved/dedicated to permit installation of the branch circuit overcurrent protective device(s) for energy storage system. (LACEC 220.41).
It looks like LA county Incorporated requirements on having Energy Storage Systems (ESS) earlier than the state and the counties that I mostly complete projects in, which are on NEC 2017. With this new ESS demand at 125% this bumps my service size to 400A with a demand of 225A (10kW added). I updated the Bus ratings to 400A with a 225A main breaker.
My question is, with the main breaker being 225A and the bus rating being 400A, does this comply with NEC2017 705.12(B)(2)(3)(a) which would allow for the PV and ESS to be located on separate circuits, anywhere on the panel? I'd place them on the very last circuits on the panel, but I'm curious about others' thoughts.
If it doesn't comply, I would definitely appreciate feedback on other ways one may go about adding the "future" ESS loads to the system while still complying with NEC requirements. Thanks!