Questions regarding 2017 NEC 700.20:


1. What is the Code definition of an emergency lighting circuit?


2. Does a branch circuit serving battery backed emergency egress lighting fixtures from a normal power panel board that also serves non-emergency lighting fixtures qualify as an emergency lighting circuit, or emergency branch circuit?
 

dkidd

Senior Member
Location
here
Occupation
PE
Questions regarding 2017 NEC 700.20:


1. What is the Code definition of an emergency lighting circuit?

700.1 Scope. The provisions of this article apply to the
electrical safety of the installation, operation, and maintenance
of emergency systems consisting of circuits and
equipment intended to supply, distribute, and control electricity
for illumination, power, or both, to required facilities
when the normal electrical supply or system is interrupted.


2. Does a branch circuit serving battery backed emergency egress lighting fixtures from a normal power panel board that also serves non-emergency lighting fixtures qualify as an emergency lighting circuit, or emergency branch circuit?

No
 

ErikaDeanda

New User
Location
New York
According to the main technical data of this type of emergency lighting, the rated voltage of the emergency light used is 2.4V, and the voltage at both ends of the battery is also 2.4V; the LED emergency light must be equipped with an emergency device - the inverter. The inverter converts DC power (battery, battery) into alternating current (typically 220v50HZ sine or square wave). Emergency power supply is generally to invert the DC battery into 220V AC. In general, an inverter is a device that converts direct current (DC) to alternating current (AC).
 