I have non high rise building that has emergency generator and has five floors residential and residential and some commercial bottom level.

Elevator cab lights and receptacles circuit should it be on emergency or standby? Is it in NEC 2017?
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have non high rise building that has emergency generator and has five floors residential and residential and some commercial bottom level.

Elevator cab lights and receptacles circuit should it be on emergency or standby? Is it in NEC 2017?

No one knows?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That the State elevator inspector web site.
If you are dealing with elevators they have they have the last word so ask them.
In our State, the electrical inspectors jurisdiction stops at the disconnect but in any event the elevator inspectors should be able to advise you.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
In our State, the electrical inspectors jurisdiction stops at the disconnect but in any event the elevator inspectors should be able to advise you.
It's the same in NC, the EI looks at the feeder(s) and branch circuit(s) installation into the first enclosure in the equipment room and stop there.