An existing single building with two services (3000A and 1600A, both 480V 3 Phase) is fed by a utility transformer located across the street. The secondaries run under the road approx 100 feet (8 and 4 sets of parallel 500 kcmil conductors with neutrals in 4 inch PVC conduits for each service). The service entrances, switchboards and grounding are currently in the basement of the building.
We plan to provide a new generator, switchgear and ATSs in the parking lot next to the utility transformer (across the street from the building). This involves interrupting the secondaries and providing new disconnects and grounding near the transformer, generator, generator switchgear and ATSs. (moving the service entrance from the basement across the street to near the transformer). We need to disconnect the neutral and ground in the basement (old service entrance location) and tie the two grounds together.
Question: The conduit/conductors under the road now become a feeder instead of service entrance conductors. Do all twelve sets of existing conductors have to be pulled out and repulled with a grounded conductor in each conduit per 250.122(F), or is it acceptable to provide a full size grounded conductor (one for each service) in spare duct bank conduits that run parallel to the existing conductors?
Is there an alternative configuration to avoid repulling existing conductors?
We plan to provide a new generator, switchgear and ATSs in the parking lot next to the utility transformer (across the street from the building). This involves interrupting the secondaries and providing new disconnects and grounding near the transformer, generator, generator switchgear and ATSs. (moving the service entrance from the basement across the street to near the transformer). We need to disconnect the neutral and ground in the basement (old service entrance location) and tie the two grounds together.
Question: The conduit/conductors under the road now become a feeder instead of service entrance conductors. Do all twelve sets of existing conductors have to be pulled out and repulled with a grounded conductor in each conduit per 250.122(F), or is it acceptable to provide a full size grounded conductor (one for each service) in spare duct bank conduits that run parallel to the existing conductors?
Is there an alternative configuration to avoid repulling existing conductors?