Re: E.M.T Conduit for Ground

Perhaps there is a city or state rule on this subject? Did the person who "called you" on this issue give you the code article that was being cited?
 

charlie

Senior Member
Location
Indianapolis
Re: E.M.T Conduit for Ground

If this feeds a service, I assume you mean service equipment. If that is the case, you are discussing service entrance conductors and you would not need a grounding conductor anyway even if it were PVC conduit. :D
 
Re: E.M.T Conduit for Ground

Thanks for you replies.
I asked him what year code book the City was currently using and he said 1999.I looked into art250.118 and their was my answer.I went to the building department and photocopied it and left him a message to call me.
He just said one of his other inspectors told him it was required.No issues on bonding locknuts.
The emt run was feeding a 200 amp sub panel from main disconnect.
Thanks Rick
 

sandsnow

Senior Member
Re: E.M.T Conduit for Ground

Rick
I applaud you for trying to learn the code. An inspector who does not try and do the same is not doing his job. The inspector in question is being lazy by just going by what another inspector said to do.
I hope it works out in your favor
 

physis

Senior Member
Re: E.M.T Conduit for Ground

I went to the building department and photocopied it and left him a message to call me.
That's a good trick. The rarest reaction I get to quoting a code to an inspector is that he actually read it. I think it would be like admitting not knowing it. :)

Edit: If some of those discussions could get to the CMP's. :p

[ December 02, 2004, 12:30 PM: Message edited by: physis ]
 
Re: E.M.T Conduit for Ground

Well this mourning he called and appoligised.He said he went and read the article when he got home.He was very nice about it.I also gave him some advise on bonding.
I always practice getting along with any inspector.I have been in business for 17 years and have never argued with one.May not always agree.
Most have pretty common sense and are just trying to do their job.Never get on their bad side or try to show them up.
Thanks Rick
 
Re: E.M.T Conduit for Ground

I would like to discuss this a bit further, not necessarily this specific installation, but the use of emt as the EGC in general. Although the code permits emt and RMC as equipment grounding conductors, there is a statement in the code which implies that this practice is not always appropriate. 250.4(A)(5) in short states there must be an effective low impedance ground fault path. The commentary on 250.133(A) in the handbook states, "if a long distance exists between a power source and utilization equipment, some of the wiring methods allowed for grounding purposes must be evaluated further." I guess this just equates to a judgment call of the electrician and/or inspector as to whether a EGC should be installed in emt? Anyone have any opinions on this? In the past i have always installed a EGC in emt. Its kind of like the push in terminals on receptacles, you can use them but do you want to or should you?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: E.M.T Conduit for Ground

I believe a properly installed metal raceway system may provide a lower impedance ground fault path than the EGC required by Table 250.122. :p
 
Re: E.M.T Conduit for Ground

Ryan, thanks for the great link, certainly lots of great discussion there i will mull over.

A while back i was helping a friend set up a hot wire foam cutting jig to "plane down" some 3" foam. Just off the top of my head without doing any calculations, i was sceptical that my variable voltage dc power supply could be adjusted low enough to prevent the power supply from 'seeing' the load, a two foot piece of wire, as a short. It turned out that the steel was such a bad conductor compared to copper that i barely had enough voltage to push a good 20 amps thru. I guess thats why i am initially hesitant to use emt as EGC. I will mull over that link and do some calculations and hopefully i can become a bit more comfortable with it. :)
 

ryan_618

Senior Member
Re: E.M.T Conduit for Ground

Yes, I was very happy with the way that discussion took off running. I would make it point to click the link in that thread that Don provided to the GEMI software. I learned quite a lot just by playing around with it.
 