Dust ignitionproof Enclosure

Status
Not open for further replies.

dst55

Member
I'm currently designing an enclosure for a Class 2 Div. 2 Group G area and trying to dechypher what NEC is trying to convey in it's statement concerning a "dust ignitionproof enclosure". My question is, Will a NEMA 4 enclosure by itself suffice for this application or would I have to add a purge? I definitely do not want to use a NEMA 9 enclosure. Thanks, dst55
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Dust ignitionproof Enclosure

What will be in this enclosure? Only arc producing or heat producing devices require dust ignitionproof enclosures. Other enclosures are only required to be "dust tight"
Don
 

dst55

Member
Re: Dust ignitionproof Enclosure

The only device going in the enclosure is an Allen Bradley PanelView 1000T HMI. I talked with "our friends" up in Boston (Quincy) and it looks like I'll be okay with a NEMA 4X without a purge. Thanks, dst55
 