Dry type transformer generator power

Status
Not open for further replies.

xguard

Senior Member
Location
Baton Rouge, LA
Someone proposed having a dry type ventilated transformer in between generator and transfer switch. The transformer would only be energized when the generator is running. Digging through instruction manuals for the transformers it looks like it's better to have them energized all the time to keep moisture out? Thoughts? Anyone have experience with having them energized intermittently?
 

TwoBlocked

Senior Member
Location
Bradford County, PA
Occupation
Industrial Electrician
You would want the same voltage coming from each feeder to the x-fer switch. Will putting the transformer between the generator and transfer switch do that?
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
If I were specifying in Louisiana, and the transformer wasn't going to be in a humidity-controlled environment, I would be reluctant to specify anything less than epoxy-encapsulated.

Keeping it energized when not in use will waste a lot of energy and money, and emit a lot of waste heat, in perpetuity.

But I have to repeat (and emphasize) TwoBlocked's question: Why not install/configure the right generator in the first place? Is there some compelling reason for installing a transformer at all?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
To emphasize the point about the generator: remember that the stator coils of a generator are essentially transformer secondary coils already. There is rarely a good reason to connect a small generator to a transformer for building backup applications.

Most larger backup generators have alternators which can be connected in a high or low voltage configuration. The generator voltage regulator then tweaks this to the correct output. You should be able to easily set the same generator up for 480/277 wye or 208/120 wye.
 

xguard

Senior Member
Location
Baton Rouge, LA
To emphasize the point about the generator: remember that the stator coils of a generator are essentially transformer secondary coils already. There is rarely a good reason to connect a small generator to a transformer for building backup applications.

Most larger backup generators have alternators which can be connected in a high or low voltage configuration. The generator voltage regulator then tweaks this to the correct output. You should be able to easily set the same generator up for 480/277 wye or 208/120 wye.
It's an 800 kw generator. Where the generator will be installed will require a run of conductors of about 150 feet.

I asked about the voltage of the generator being changed and was told it couldn't be. I'll bring that up again. After I saw the layout though I thought maybe 480 would be better given the distance.
 
I asked about the voltage of the generator being changed and was told it couldn't be.
Might mean they've never checked, might also mean that where they use it now is 480 and they think this change takes too long (at that size, I'll assume it's not portable since that wasn't mentioned).

Go over and take a look inside the cabinet, also get the make/model specifics and look it up online (in this case, don't take their word for it).
 

xguard

Senior Member
Location
Baton Rouge, LA
Might mean they've never checked, might also mean that where they use it now is 480 and they think this change takes too long (at that size, I'll assume it's not portable since that wasn't mentioned).

Go over and take a look inside the cabinet, also get the make/model specifics and look it up online (in this case, don't take their word for it).
I contacted Cummins. They recommended not swapping it to 208 due to the size and number of conductors we'd need.
 

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
You spoke of keeping the transformer 'warm' to avoid difficulties with moisture damage. What about the generator? Any source of waste heat that could keep them both toasty? Exhaust from the A/C?? (have to watch the moisture with that one...)
 