Coachmike

Member
Location
Morris County, NJ
Occupation
Electrical Contractor
Have a client with a machine shop who swears his 3 phase machines are negatively impacted by the delta 240v (high leg) feeding his 3 phase equipment. Can a power supply/ drive be affected by the high leg? (They are 3 wire 3 phase machines)
 

Attachments

  • image1 (3).jpeg
    image1 (3).jpeg
    212.9 KB · Views: 16
  • image0 (4).jpeg
    image0 (4).jpeg
    218.8 KB · Views: 16
What does "negatively affected" mean?

If the machine is designed for a wye connection with 120v phase-to-ground, it might have difficulty with the higher phase-to-ground of the high-leg (usually if there are either surge-suppressors connected to ground or it uses the ground as a bootleg neutral for some controls).

This is another case of "Ask the manufacturer" :).
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
I
Have a client with a machine shop who swears his 3 phase machines are negatively impacted by the delta 240v (high leg) feeding his 3 phase equipment. Can a power supply/ drive be affected by the high leg? (They are 3 wire 3 phase machines)
If there are no Line-Neutral loads within the drive nothing should be seeing the high leg voltage 208volt to ground.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
A couple of years ago, I was hired to add a third B-B transformer and re-wire, to convert an existing open-delta boost set-up to a wye boost set-up for a 240v machine that wouldn't accept the uneven voltages, even though there was no load neutral.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
A couple of years ago, I was hired to add a third B-B transformer and re-wire, to convert an existing open-delta boost set-up to a wye boost set-up for a 240v machine that wouldn't accept the uneven voltages, even though there was no load neutral.
what is an open delta boost setup?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
The normal rule of 'line-line loads don't care about line-ground voltage' gets a bit broken when you talk about motors on drives. The reason is because of 'parasitic' line-ground parts of the circuit.

The big one will be the TVS devices which are often connected between line and ground on the input of the VSD. This is far more of a problem on 480V drives, where the TVS devices are designed for nominal 277V to ground, and will pop on a corner grounded delta, and will likely try to create a ground for an ungrounded system. Not sure that this will be a problem for a high leg 240V system, but as noted above 'ask the manufacturer'.

Another aspect of parasitic line-ground connections is the capacitance of the motor winding to the frame. The high frequency modulation of the VSD creates a high frequency current from winding to frame, and this current is trying to get back to the transformer source via the transformer ground point. I don't know if asymmetric line to ground voltages meaningfully alter this current, but I could imagine that such would introduce a large 120Hz ripple in this ground current that might impact other equipment.

-Jon
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Commonly, 'open delta' is used to describe a power company supply configuration where only two legs of the delta are used for a supply.

But the term is also used to describe an autotransformer configuration used to buck or boost a three phase supply using two transformers. The second use of the term is what post 7 shows.

-Jon
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor

kwired

Electron manager
Location
NE Nebraska

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It is also possible to use three autotransformers to create a "full delta" in which all three output circuits are symmetric. But if you have acorner grounded input, the output will be corner ground referenced but none of the output lines would actually be at ground potential.
If you have a delta circuit fed from a wye source, then the boosted circuit would have the same center point ground reference supplied by the source end.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Getting back to the subject, this issue has nothing to do with it being a “high leg” system, it’s about being a delta system. In the case of a 240V delta system, Jon’s last paragraph is the issue for the most part. Almost all drives are made expecting a solidly grounded Wye source. They will usually have “common mode capacitors” to handle the ground noise issues, but in a delta system with no direct reference to ground on one phase, that noise builds up and affects other things, including the drive electronics. The safe bet if you already know there is an issue is to use a “drive isolation transformer” to feed the drives. It will be 240v input, 240/139V grounded Wye output. You are not using the 139V for anything, it’s just to establish a solidly grounded neutral feeding the drives.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
It is also possible to use three autotransformers to create a "full delta" in which all three output circuits are symmetric.
So let's see, this would cause the group of phase angles to rotate relative to the supply, yes?

I.e. Say you have 3 identical single coil transformers A, B, C, and each has connections A0, AX, and A1, where AX is X fraction of the turns from A0 to A1. Then for bucking you wire the supplies to A0=C1, B0=A1, and C0=B1. Then AX, BX, CX are your bucked voltages, and a little geometry tells you the bucked voltage and rotation relative to the supplies (if you care). Conversely for boosting you swap the roles of the X connections and the 1 connections.

Cheers, Wayne
 