Do I need an EGC?

Status
Not open for further replies.

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Because it violates 250.24(A)(5) and 250.32.
Excellent references, that show bare neutrals can't touch messengers & raceways, or violate separation of EGC & Neutral (Grounded).

Now see photo's below. Left weather-head service drop, and Right weather-head feeder.

I believe this is Triplex with all insulated conductors, one is marked White (for neutral), and has bonded feeder-side EGC to messenger.

That braded steel messenger does not comply with Table 250.122 for EGC sizing, but it still works, and passed inspection.
 

Attachments

  • Triplex-1.jpg
    Triplex-1.jpg
    55.2 KB · Views: 20
  • Triplex-2.jpg
    Triplex-2.jpg
    37.7 KB · Views: 20
  • Triplex-2back.jpg
    Triplex-2back.jpg
    32.8 KB · Views: 21
Last edited:

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
They also drove 2 ground rods, barely 6ft apart.
 

Attachments

  • Triplex-Rods.jpg
    Triplex-Rods.jpg
    99 KB · Views: 3

paulengr

Senior Member
Your boss is describing a peg ground. Edison caused some severe hazards doing this. You can only have one ground connection, one system bonding jumper, unless you create a separately derived system. And from there everything must be bonded. What you describe breaks the bonding, or adds a second system bonding jumper. Either way it’s a Code violation and a safety hazard since there is no low impedance path anymore back to the transformer neutral. So then no way to trip on ground fault,
 