djd

Senior Member
This is a theory question , we doing a solar project and wanted to know , DC wiring is not subject to derating correct ; beyond typical pipe fill and cable tray capacity. I cant name the type of wire but it is pv wire with a pretty thick insulation.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
This is a theory question , we doing a solar project and wanted to know , DC wiring is not subject to derating correct ; beyond typical pipe fill and cable tray capacity. I cant name the type of wire but it is pv wire with a pretty thick insulation.
There is one type of wire for which you do not need to use the temperature adder on rooftops - XHHW-2 (the exception to 310.15(B)(3)(c)), but there is no distinction between AC and DC wiring as far as derating ampacity is concerned.
 

djd

Senior Member
djd

djd

Thanks for all the insight on this , I really wasnt sure couldnt find it in the code book
 