disconnect at meter base?

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, look here:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:

(1) Service disconnects marked as follows:
EMERGENCY DISCONNECT, SERVICE DISCONNECT

(2) Meter disconnects installed per 230.82(3) and marked as follows:
EMERGENCY DISCONNECT, METER DISCONNECT, NOT SERVICE EQUIPMENT

(3) Other listed disconnect switches or circuit breakers on the supply side of each service disconnect that are suitable for use as service equipment and marked as follows:
EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT

Markings shall comply with 110.21 (B).
 