What is the difference between PV breaker and a circuit breaker? I am trying to learn and your input would be greatly appreciated.
Modern circuit breakers that are marked Line and Load are not tested and Listed for backfeed. Most special purpose circuit breakers, such as GFID, are not listed for backfeed. There are several threads on this.One other interesting thing about the specific application of a PV breaker for backfeed from a grid interactive inverter is that the direction of power flow is from the terminals to the panel bus, but when open it has power only on the bus side. This leads to some disputes on whether you can use a breaker with the wire terminals marked as "output" for this purpose.
A while back someone posted a link to a youtube video showing the same knife switch opening AC and DC circuits with the same voltage and current. Very different results for the AC and DC circuits.If you are referring to a DC breaker, a lot. An AC breaker merely has to open the contacts enough and cool the arc so that at current zero the are can’t restrike. A DC breaker has to totally quench the arc which is much more stable than AC. That’s why DC breakers are huge for their ratings.
I am a newbie and trying to understand solar pv ac disconnect switch. There is an interactive inverter that goes to the load in side (bottom) of the ac disconnect. There is the main ac coming to the top of the ac disconnect (line in), Ok I understand. Then there is a supply/line side tap (with insulated limiters) coming from the load out of ac disconnect (bottom). to the main disconnect to the meter side. Ok I understand. What I don't understand is how pulling the ac disconnect switch to off cuts the inverter ac to the main service panel. Can someone enlighten me? Is there another set of wires from the load out going to the main panel?
Most general purpose circuit breakers don't have a specific line and load side either though. Some with integral electronic functions however might as those functions might be powered by the line side or the load side and need to be connected accordingly.One other interesting thing about the specific application of a PV breaker for backfeed from a grid interactive inverter is that the direction of power flow is from the terminals to the panel bus, but when open it has power only on the bus side. This leads to some disputes on whether you can use a breaker with the wire terminals marked as "output" for this purpose.