I have 7 #12 conductors an 5 #10 conductors all thhn in 1 inch emt.
The run is only 20 feet long he says I have to derate the conductors due to conduit overfill, I don't think so according to the conduit fill chart. Is the
Inspector wrong as I suspect? Thanks Guys.