I will be running circuits for new Air Conditioning. One for the compressor and one to the air handler.

The calculate as such:

Compressor: #12 wire 75 degrees with 25A breaker MCA 22.7 MOP 25A
Air handler: #14 wire with 15A breaker MCA 6.5 MOP 15A

My knockouts in the main electrical panel are limited. I would like to run all the conductors out the panel in FMC to a junction box and then split out the two circuits. There will be 4 current-carrying conductors in the ¾’ FMC (plus two ground conductors) from the panel to the junction box(10-12 feet). Do I need to derate the ampacities of the conductors to do this?

If the #12 need to be derated, the #12 wire could carry: 25 * .8 = 20A The MCA is 22.7 A. Do I need to up the wire to #10?

The #14 can carry 20A. Derated 20*.8 = 16 amps MCA is 6.5A OK?

After the first junction box (+- 10 feet), there will only be 2 current carrying conductors in a single conduit. Should I keep the smae wire size from the outcome above. From the junction box to the equipment is only another 15' max.

Thanks for your help.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am closing this thread, in accordance with the Forum Rules.
This site is designed for:
  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
* This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
If you feel this action to be in error, feel free to contact me via PM to explain. Reminder to all members, if you see a questionable post, feel free to report it by clicking "Report" at the bottom left corner of the post.
 
Status
Not open for further replies.
Top