Dedicated isolated outlets

Status
Not open for further replies.

goofy78270

New member
What are the requirements for a dedicated isolated outlet? Does it have to be orange or just an orange triangle and are these required?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Dedicated isolated outlets

406.2(D)

(D) Isolated Ground Receptacles Receptacles incorporating an isolated grounding connection intended for the reduction of electrical noise (electromagnetic interference) as permitted in 250.146(D) shall be identified by an orange triangle located on the face of the receptacle.
Roger

[ September 23, 2005, 06:40 PM: Message edited by: roger ]
 