Is there anything in the code regarding running a dc power cable through a wall?
Camera is outside... receptacle is adjacent to camera inside
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
You say DC power cable then say there is a receptacle inside. Is there a "wall wart" power supply plugged into the receptacle and a cable from it going out to the camera? Likely then the DC is class 2 and there is no problem running it through the wall. Assume a CL2 listed cable.