Can anyone tell me a ballpart # to run (3) sets of 4#600KCM, 4" PVC conduit for 100 linear feet underground?
I am thinking 60K, allowing $200 per linear feet of of 4#600 KCM feeder run... so, 3 sets x $200 per feet x 100 feet = $60,000...
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
600 kcm copper is about $20/foot.

So about $250 per foot for the wire, or a total of maybe $25,000 for the wire.

What are you planing to do for the ground conductor? Will need to be a full sized ground wire in each conduit.

2/0 ground X 300 feet is about $5/foot so another $1500.

4#600 plus ground will take probably a 5 inch PVC conduit so add 500 feet of that. Maybe $20/foot, so $10,000.

Trenching and filling is probably about $100 a foot by the time you get done with it. Maybe $10,000 contracted out.

So close to $50,000 in parts and trenching not counting your labor and markup.

Just my guess.
 

anbm

Senior Member
600 kcm copper is about $20/foot.

So about $250 per foot for the wire, or a total of maybe $25,000 for the wire.

What are you planing to do for the ground conductor? Will need to be a full sized ground wire in each conduit.

2/0 ground X 300 feet is about $5/foot so another $1500.

4#600 plus ground will take probably a 5 inch PVC conduit so add 500 feet of that. Maybe $20/foot, so $10,000.

Trenching and filling is probably about $100 a foot by the time you get done with it. Maybe $10,000 contracted out.

So close to $50,000 in parts and trenching not counting your labor and markup.

Just my guess.
Thanks, no ground wire, forgot to mention, this is service feeder, no ground wire.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
If you have 100 feet of pipe underground, why are you figuring only 100-ft runs of wire?

You gonna terminate right at the end of the pipe?

Don't you need at least 5 feet on each end to turn up and terminate?
 