Correct wire gauge for 70'

Status
Not open for further replies.

ispconsultant

New member
I am installing a 15KW Nat gas Guardian generator.
The transfer switch that comes with it is wired with #6 for the hots, and a #8 for the common in a pre-wired bx cable setup that is 30' long.

The problem is that I have to run about 65-70' to the generator.
The generator has a 65A/220v breaker, so is it acceptable to put in a junction box and splice in the additional length using #6? Is 70' too long for running 65A/220v in a conduit?

From what I can tell, the voltage drop should be acceptable:
240V 1phase, ambient temp 25C, 70' long 1 way, and 65A load would be 4.4v drop, with 1.8% right? The conductor temp is 69C, so using 90C rated wire over this length should be ok, right?
I used the voltage drop calc at http://www.electrician2.com/calculators/vd_calculatoradv.htm

I guess I am just looking for someone to double check my numbers here.
Thanks in advance.
 

iwire

Moderator
Staff member
Location
Massachusetts
Are you an electrician?

Are you really doing the installation or are you just checking the work to be done by an electrician.

I am closing this thread for now.

We can not help DIY types here, if I am mistaken you can PM me and let me know.
 