Connecting lightning protection to service

Status
Not open for further replies.

pikie29

Member
I'd like to get some input about connecting lightning protection to the main service ground rod. The local inspector says that it must all be connected together equalizing all potential, but I would think you would want to direct any lightning as far from the service as possible. any thoughts?
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Connecting lightning protection to service

To keep the two systems separate is asking for all your electronic to explode, burn down your house down, and electrocute the occupants. If you left the two separate your coaxes, EGC, shielded cables, etc would try to equalize the potential between the two systems during a lightning fault via the mechanism of step potential differences.

Same principal applies to isolated grounding receptacles. They cannot be on serarate grounding system either.

[ July 14, 2005, 12:21 PM: Message edited by: dereckbc ]
 

pikie29

Member
Re: Connecting lightning protection to service

Are you saying it would try to equalize through the earth between the lightning ground rods and the service ground rod?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Connecting lightning protection to service

Are you saying it would try to equalize through the earth between the lightning ground rods and the service ground rod?
It can try to equalize with "side flashes". That is small lighting bolts jumping from one grounding system to the other.
Don
 