I have a machine that has a 480 delta to 380 wye transformer for it's supply.
My building is giving me a 480 wye to the machine... can this work or do I need to change the machine transformer.

Thanks...
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You can connect a transformer delta to a wye system. Just ignore the neutral on the supply.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The 480 Delta is just the configuration of the three coils on the primary side. The transformer primary doesn't care that the 3Ø originates in a Wye system.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
You can connect a transformer delta to a wye system. Just ignore the neutral on the supply.
I would be looking to see if the machine needs 50 or 60 hertz. 380 is an overseas voltage that is usually 50 hertz.
 