Hi all,
I recently helped my dad install a solar system. Everything seemed fine at the inspection, until the inspector started doubting the fire setbacks. After I provided proof of set back measurements, the inspector later said, "you can't run conduit in the fire set back". It seemed like a random statement, almost to save face. It was especially weird considering there are homes in the neighborhood with solar and similar conduit runs. Just to give some details there's a east and west mounting plane. A 3/4 conduit pipe is linking the 2 arrays. We have 3 feet total space between the arrays, but he's saying you cant run conduit across the array?
I provided IFC 1204.2
"Not fewer than two roof pathways extending from the lowest edge to the ridge and not less than 36 inches (914 mm) wide, shall be provided on all buildings with solar system installations. Not fewer than one pathway shall be provided on a street or driveway side of the roof. Pathways shall be over areas capable of supporting fire fighters accessing the roof. Pathways shall be located in areas with minimal obstructions such as vent pipes, conduit, or mechanical equipment."
He said that still wasn't acceptable.
Upon more research I noticed that IFC 2012 605.11.2 Locations of DC conductors states:
"Conduit, wiring systems and raceways for photovoltaic circuits shall be located as close as possible to the ridge or valley and from the hip or valley as directly possible to an outside wall to reduce trip hazards and maximize ventilation opportunities. Conduit runs between sub arrays and to DC combiner boxes shall be installed in a manner that minimizes the total amount of conduit on the roof by taking the shortest path from array to the DC combiner box"
My dad's city is in IFC 2018. Do new codes cycles acknowledge previous stipulations? Any previous experience with this? It sounds like he's just splitting hairs, but I want to be sure?
I recently helped my dad install a solar system. Everything seemed fine at the inspection, until the inspector started doubting the fire setbacks. After I provided proof of set back measurements, the inspector later said, "you can't run conduit in the fire set back". It seemed like a random statement, almost to save face. It was especially weird considering there are homes in the neighborhood with solar and similar conduit runs. Just to give some details there's a east and west mounting plane. A 3/4 conduit pipe is linking the 2 arrays. We have 3 feet total space between the arrays, but he's saying you cant run conduit across the array?
I provided IFC 1204.2
"Not fewer than two roof pathways extending from the lowest edge to the ridge and not less than 36 inches (914 mm) wide, shall be provided on all buildings with solar system installations. Not fewer than one pathway shall be provided on a street or driveway side of the roof. Pathways shall be over areas capable of supporting fire fighters accessing the roof. Pathways shall be located in areas with minimal obstructions such as vent pipes, conduit, or mechanical equipment."
He said that still wasn't acceptable.
Upon more research I noticed that IFC 2012 605.11.2 Locations of DC conductors states:
"Conduit, wiring systems and raceways for photovoltaic circuits shall be located as close as possible to the ridge or valley and from the hip or valley as directly possible to an outside wall to reduce trip hazards and maximize ventilation opportunities. Conduit runs between sub arrays and to DC combiner boxes shall be installed in a manner that minimizes the total amount of conduit on the roof by taking the shortest path from array to the DC combiner box"
My dad's city is in IFC 2018. Do new codes cycles acknowledge previous stipulations? Any previous experience with this? It sounds like he's just splitting hairs, but I want to be sure?