Conduit / Iron pipe gas on top of Concrete

Status
Not open for further replies.

MJRobinson

Member
Location
Chico, CA, USA
Hello,

I'm looking for the code rules on conduit. We have a customer with a house built on lava cap, almost impossible to trench it.

Can we run surface mounted conduit/gas line along the edge of a slab without bollards? It would be 18" from a fence so I don't see a tripping hazard.

I'm thinking no go, if we do have to have bollards, how often, its 29' run.

Thoughts?

Mike
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What type of conduit? If you ran RMC where it wasn't a tripping hazard I don't see an issue.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds fine to me RMC is permitted to be run exposed, around here we all types of interesting ways that guys run conduit for generators especially when they need to at least 5' from the house. What is watertight rigid?
 