Gentlemen,

I have just gotten out of a debate with a local contractor about conduit fill for a piece of 1 inch EMT. I have a subpanel that needs to be brought up from a 60A, single phase feed to a 100A single phase feed. Existing there is a 1 inch EMT conduit from the MDP to the sub-panel. Distance is around 140 feet. I asked the contractor to use the existing conduit and pull in the required new wire for the job. He said he would have to run new conduit because the conduit would be too full and its against code. I disagree. Here's my calculations:

Vd = 11.1 x 280 x 100 / (52620) = 5.91 v

5% of 120 v = 6 volts (Can use a #3 for conductors)


From Chapter 9, Table 4 and Table 5 (2002 NEC)

1" EMT has an area of 222 mm^2 (at 40% fill)

#3 THHN/THWN has an area of 62.7 mm^2

#8 THHN/THWN has an area of 23.61 mm^2

so...

3 x 62.7 mm^2 = 188.1 mm^2
1 x 23.61 mm^2 = 23.61 mm^2

Grand Total of 211.71 mm^2 in wire

Since 211.71 mm^2 is less than 222 mm^2, the combination of (3) #3's and (1) #8 can be pulled an remain under the 40% mark required by Chapter 9, Table 1.

Anyone agree or disagree? :confused:


PS - I know its not the ideal circumstance and an 1.25" conduit would be nice, but under the circumstances that is not feasible.
 

ryan_618

Senior Member
Re: Conduit Fill Calcs

Agree.

I used the inches values because I'm metric dumb, and here is what I came up with:

1" EMT at 40%=0.346 sqaure inches
#3=0.0973 square inches
#8=0.0366 sqaure inches
So,

0.0973*3=0.2919
+0.0366=0.3285, which is less than 0.346, and therefore you comply.


BTW: Make sure you eat your wheeties before you pull it!!!
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Conduit Fill Calcs

Perhaps the contractor has doubts about getting this wire in a 140' of conduit.

Just because the book says it will fit does not mean you can get the wire in.

This is where experience comes in, knowing what is possible.

How many bends between pull points, are there LBs to deal with?

I would not attempt to put three 3 AWGs and an 8 AWG in 140' of 1" raceway even if the code says it is can be done.

The contractor may have misstated the code as a way to convince you this is a bad idea.
 

bphgravity

Senior Member
Location
Florida
Re: Conduit Fill Calcs

I also agree all your numbers look good except for the 11.1 value for "K".

The actual "K" of #3 is 12.8919-ohms. (R x cm / 1000) This means you will exceed 5% voltage drop as specified by you. 5% is on the high end for just the feeder conductors. However, this shouldn't be an issue considering the load will probably never be the full 100-amperes. :)
 