(2) Feeders. Fire pump supply conductors on the load side
of the final disconnecting means and overcurrent device(s)
permitted by 695.4(B), or conductors that connect directly
to an on-site standby generator, shall comply with all of the
following:
(a) Independent Routing. The conductors shall be kept
entirely independent of all other wiring.
(b) Associated Fire Pump Loads. The conductors shall
supply only loads that are directly associated with the fire
pump system.
(c) Protection from Potential Damage. The conductors
shall be protected from potential damage by fire, structural
failure, or operational accident.
(d) Inside of a Building. Where routed through a building,
the conductors shall be installed using one of the following
methods:
(1) Be encased in a minimum 50 mm (2 in.) of concrete
(2) Be protected by a fire-rated assembly listed to achieve
a minimum fire rating of 2 hours and dedicated to the
fire pump circuit(s)
(3) Be a listed electrical circuit protective system with a
minimum 2-hour fire rating