Continuation of previous post:
Contracted $10,000 complete rewire of house including replacing conductors:
Living room Receptacle:
15A 125V Duplex TR receptacle
Body of receptacle wrapped with tape -- often indicator of bush-league player
ground wires twisted together --- no listed splicing device
metal box not grounded
no cable clamps
NM cable pokes through box-clamp style knockouts
Two S1 switches in ganged metal box
no ground wires
box not grounded
use white/black as switch loop
white is feed
white is not re-identified
Fan
Fan box used
Fan Box ground under screw, screw not tightened
Dryer1
old 3 wire SE cable as feed -- not replaced
3-wire not 4-wire receptacle
Dryer2
new 10/3 w/g cable
receptacle laying on floor with a couple feet of cable going into wall
200A panelboard
subfeed from Main Disconnect 200A CB in combo meter socket
fed into 200A panelboard main breaker (OK)
Neutrals on left bar; grounds on right bar;
neural and grounds connected to horizontal bar connecting two vertical bars
grounds connected to lug screwed into cabinet.
Unable to locate "green" Screw bonding cabinet
so box may not be bonded; neutrals / grounds not separated in subfed box
No AFCI CBs (2011 after Jan 1, 2014)
20A CBs with #14 (presumably non-motor) circuit wires.
Numerous Junction boxes in basement ceiling connecting new NM to old wiring (Remember replace all conductors)
Junction box that was checked as not bonded to ground wire (surprise)
Left in disgust!
Contracted $10,000 complete rewire of house including replacing conductors:
Living room Receptacle:
15A 125V Duplex TR receptacle
Body of receptacle wrapped with tape -- often indicator of bush-league player
ground wires twisted together --- no listed splicing device
metal box not grounded
no cable clamps
NM cable pokes through box-clamp style knockouts
Two S1 switches in ganged metal box
no ground wires
box not grounded
use white/black as switch loop
white is feed
white is not re-identified
Fan
Fan box used
Fan Box ground under screw, screw not tightened
Dryer1
old 3 wire SE cable as feed -- not replaced
3-wire not 4-wire receptacle
Dryer2
new 10/3 w/g cable
receptacle laying on floor with a couple feet of cable going into wall
200A panelboard
subfeed from Main Disconnect 200A CB in combo meter socket
fed into 200A panelboard main breaker (OK)
Neutrals on left bar; grounds on right bar;
neural and grounds connected to horizontal bar connecting two vertical bars
grounds connected to lug screwed into cabinet.
Unable to locate "green" Screw bonding cabinet
so box may not be bonded; neutrals / grounds not separated in subfed box
No AFCI CBs (2011 after Jan 1, 2014)
20A CBs with #14 (presumably non-motor) circuit wires.
Numerous Junction boxes in basement ceiling connecting new NM to old wiring (Remember replace all conductors)
Junction box that was checked as not bonded to ground wire (surprise)
Left in disgust!