Clearance of manufacturer live parts to enclosure

Status
Not open for further replies.
As always when I post here, I need an answer on the fly.

What is clearance of live parts, including our terminations to the enclosure and other metal parts? I appreciate the help.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
As always when I post here, I need an answer on the fly.

What is clearance of live parts, including our terminations to the enclosure and other metal parts? I appreciate the help.
This should not be an issue for you because the equipment that you're terminating to should have this already incorporated into its design.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You can use Table 408.56 in the NEC as guidance, but the product standards, and not the NEC govern this issue.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Clearance to terminals for wires exiting an enclosure are also governed by "wire bending space", so without specifics on what you are referring to, there is no single answer.
 