Class 1 Div II Approved Motor Cabling Materials for 480V, 3 PH Motor Connections

Status
Not open for further replies.

Bob Lemke

Member
Location
Dayton, Ohio
Occupation
Controls Engineering
Getting some info on the possible use for a TC-ER rated cabling. This cable would exit through a perimeter barrier from a hazardous area to non-hazardous area through a conduit to be potted at final installation for a 10HP 480V, 3 PH motor connection. Looking for any other cable rated suggestions. Thank you.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Suitable alternate multiconductor cables are listed in Section 501.10(B)(1)(5).

BTW you have the Roman and Arabic numerals reversed; it's Class I, Division 2.
 