Class 1, Div 2 required to be explosionsproof?

Status
Not open for further replies.

nmui

Member
Does anyone know if an explosionproof device automatically make it a Class 1, Div 1 device? Are there instances where a device is rated for both Class 1, Div 2 and explosionproof, but not need a Class 1, Div 1 rating?
 

pwhite

Senior Member
Re: Class 1, Div 2 required to be explosionsproof?

explosion proof devices typically have their rating listed on the device and paperwork that comes with the device.

just because its explosion proof doesn't mean that its approved for class 1 div 1. there are class 1,2,3 environments as well as groups a-g.

look at nec 2002 section 500 for your application.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Class 1, Div 2 required to be explosionsproof?

pwhite,
Actually the term "explosion proof" only applies to Class 1 locations. Class 2 locations use the terms "dust ignition proof" and "dust tight". Class 3 locations use the term "dust tight".

nmui,
The equipment cannot just say "explosion proof". It must be marked for the Division and Group that it can be used in. In most cases if the words "explosion proof" appear on the equipment, the equipment will be labeled for Class 1 Division 1 locations.
Don
 

pwhite

Senior Member
Re: Class 1, Div 2 required to be explosionsproof?

don,
thank you for the clarification.
i didn't have time to look the classifications up when i posted and was making a general statement about the various classifications.
 