How can a manufacturer provide an FM approved device (Non-Incendive, CL1, DIV2, GPA, B, C, D, T4 analyzer/transmitter) that comes with its own (non-explosion-proof, non-purged) enclosure with several RELAY output contacts within and power supply input requirements of 24-253V (ac/dc) in light of 2005 NEC501.10(B)(4) and 501.105(B)(1)?
On the label is
"WARNING - Explosion Hazard - DO NOT DISCONNECT EQUIPMENT UNLESS POWER HAS BEEN SWITCHED OFF OR THE AREA IS KNOWN TO BE NON-HAZARDOUS."
AND
"WARNING - BONDING BETWEEN CONDUIT IS NOT AUTOMATIC AND MUST BE PROVIDED AS PART OF THE INSTALLATION. SEE INSTALLATION INSTRUCTIONS."
On the label is
"WARNING - Explosion Hazard - DO NOT DISCONNECT EQUIPMENT UNLESS POWER HAS BEEN SWITCHED OFF OR THE AREA IS KNOWN TO BE NON-HAZARDOUS."
AND
"WARNING - BONDING BETWEEN CONDUIT IS NOT AUTOMATIC AND MUST BE PROVIDED AS PART OF THE INSTALLATION. SEE INSTALLATION INSTRUCTIONS."