Re: Circuit Breaker Conductor Temperature Rating
Tim, The way I look at it when it comes down to the bottom line it's no big deal, 60 vs 75degC. Take a look at the 2002 NEC ART 240.4(D) Small conductors, #14,#12, and #10. Except for other derating factors up to 10 AWG size 75degC rated wire is applied as if were 60degC anyway. Isn't THHN 90degC rated anyway? It's still applied as 60degC. As such, there really isn't any advantage of using 75degC or 90degC rated wire because of the limitation as included in art 240.4(D) if derating factors aren't an issue.
Even so at the other end of the circuit is often a device such as a light fixture that calls for 90degC rated wire when 60degC won't work.
Also, keep in mind that larger breakers have been supplied with 75degC terminals for quite some time where 90degC rated THHN wire is applied at 75degC, again this is without any derating factors taken into consideration.