I have cell tower site that has AC panelboard 120/240V single phase. Feeder breaker of panelboard 240V single phase feeds Ericsson Enclosure 6160AC. Currently its loaded to 14.4kw at 240V. Feeder breaker provided is 100A.
I am wondering feeder breaker size should be 80A not 100A. However it can be 100A but I am not sure about the rating of Ericsson Enclosure 6160AC. Has anyone worked with that enclosure?