CEE ground

Status
Not open for further replies.

Teslaman

New User
Location
Pulaski,Tn
Occupation
Electrical Super
Took over a partial job. CEE is sticking out from the side of the foundation. Figure i need to slit concrete and tuck inside to grounding bar, or, should i just run it inside my ct cabinet to my mdp?
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I would just connect electrode conductor to what you have sticking out. Also the conductor for CEE doesn't need to be larger than 4 copper.
 