CEC Table 5c vs 310.15(B)(3)(a)

Status
Not open for further replies.

zylezuin

New member
Can anyone explain why the two tables (NEC and CEC) referenced in the title are so drastically different? 1-6 conductors are the same, but after that NEC is significantly more conservative. The tables for a #12 90c THHN (T90 equivalent) in both codes give a 30A starting value. For 20A circuits you need to move to a #10 after the 9th conductor in NEC, but not until the 25th in CEC? What am I looking past? Thanks!


Table 310.15(B)(3)(a) NEC 2014
Number of conductors vs derating value
4-6 = 80%
7-9 = 70%
10-20 = 50%
21-30 = 45%


Table 5C
Number of conductors vs derating value
4-6 = 80%
7-24 = 70%
25-42 = 60%
 

Adamjamma

Senior Member
Could it be due to the normal temperatures? Canada does not hit the higher summer temps as hit by parts of the USA, so the wires do not face the higher ambient temperatures??
Just thinking... know Jamaica is considering smaller groupings due to higher climate temps..
 

Eddy_Current

Member
Location
Canada
Could it be due to the normal temperatures? Canada does not hit the higher summer temps as hit by parts of the USA, so the wires do not face the higher ambient temperatures??
Just thinking... know Jamaica is considering smaller groupings due to higher climate temps..

I do not know why they are different, but Outside temperatures have nothing to do with it.

It gets a lot hotter here here than many assume and besides, the insides of houses and building are climate controlled so our wires are at the same ambient temp as yours.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The NEC used that same table for a long time, but it specified that it only applied where the conductors had a 50% load diversity. That was not a defined term and when they attempted to define it, they could not agree on a definition. That table is still in the NEC but not as a code rule, it is in Informative Annex B as Table B.310.15(B)(2)(11).
I believe the Massachusetts amendment also uses that table.

Does the Canadian Code say anything about load diversity for the application of that table?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In the 1990 code the ampacity adjustment rule was in Note 8 to the 0-2000 volt ampacity tables. That edition had two columns with differing derating values. Column A was for installations with a 50% load diversity where you had over 9 current carrying conductors. Column B was the same as we have in the code now. In the 1993 code the table only had the column without load diversity in Article 310, and the information from the other column was relocated to Annex B.
 

Eddy_Current

Member
Location
Canada
The NEC used that same table for a long time, but it specified that it only applied where the conductors had a 50% load diversity. That was not a defined term and when they attempted to define it, they could not agree on a definition. That table is still in the NEC but not as a code rule, it is in Informative Annex B as Table B.310.15(B)(2)(11).
I believe the Massachusetts amendment also uses that table.

Does the Canadian Code say anything about load diversity for the application of that table?

What is load diversity?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What is load diversity?
No one could really define it and that is why that table is no longer a code rule.
50% load diversity could mean 50% of the conductors in the raceway or cable loaded at 100% of their rating, or could be all of the conductors loaded to 50% of their rating.
The second one would make more sense as that would be less heat produced from the I²R losses.
Either way, it would be difficult to enforce.
 

Eddy_Current

Member
Location
Canada
No one could really define it and that is why that table is no longer a code rule.
50% load diversity could mean 50% of the conductors in the raceway or cable loaded at 100% of their rating, or could be all of the conductors loaded to 50% of their rating.
The second one would make more sense as that would be less heat produced from the I²R losses.
Either way, it would be difficult to enforce.

Our Table 5c only applies to current carrying conductors. (Power and lighting conductors)

True neutrals (conductor that would only carry the unbalanced current), bonds, grounds and control conductors do not have to be counted when determining ampacities.

CEC 4-004
 