Can SER be run through floors of a type IV construction building

Status
Not open for further replies.

tselectric617

New User
Location
ma
Occupation
electrician
im doing a 3 story apartment building that has a 1200 amp 3 phase 120/208v main service with meter stacks for the whole building all in one electric room on the first floor. is it code to use ser to feed all the apartments on all the floors from the main electric room. the wire will be protected from physical damage being in the walls. there is no plenum ceilings anywhere on this job. the feeders would have to run through the fire rated ceilings on the apartments and through the floors. the question is can you run ser though out this building or does it have to be mc because it passes though multiple floors? this job is done in using the MA amendments

NEC 334.10(2) says we can run NM cable in construction types III, IV, & V.
 