Attached sketch shows feeder FDR#1which feeds meter stacks in multi family dwelling.
Each meter stack feeder feeds individual dwelling unit.
I am trying to size FDR #1 and was wondering if I can use NEC 2014 Section 220.84(A) or not. NEC 2014 Section 220.84(A)(2) each dwelling unit has electric cooking equipment and NEC 2014 Section 220.84(A)(3) each dwelling unit has electric HVAC. However I am confused about NEC 2014 Section 220.84(A)(1) because FDR #1 feeds multiple dwelling units and each meter stacks feeder feed to each dwelling unit.
So can I use NEC 2014 section 220.84(A) to size FDR#1? Please anyone here can help me with their opinion regarding this matter
Each meter stack feeder feeds individual dwelling unit.
I am trying to size FDR #1 and was wondering if I can use NEC 2014 Section 220.84(A) or not. NEC 2014 Section 220.84(A)(2) each dwelling unit has electric cooking equipment and NEC 2014 Section 220.84(A)(3) each dwelling unit has electric HVAC. However I am confused about NEC 2014 Section 220.84(A)(1) because FDR #1 feeds multiple dwelling units and each meter stacks feeder feed to each dwelling unit.