Can anyone verify if this is a listed electrical fitting, or should it have water running through it?

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The missing locknut tells me it was put in after the cabinets were hung, but with running threads, it could be there.

The wire looks big enough that there should be bushings. In any case, it looks amateurish.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Not sure about PVC running thread, but I purchased rigid running thread for that type of application a number of times...however we always used 4 locknuts, and two bushings.
 

danielk54

Member
Location
Indiana
The missing locknut tells me it was put in after the cabinets were hung, but with running threads, it could be there.

The wire looks big enough that there should be bushings. In any case, it looks amateurish.
amateurish was an understatement, you should see the rest of this mess....
From a code perspective, how would you cite the missing locknut ?
 

Frank DuVal

Senior Member
Location
Fredericksburg, VA 21 Hours from Winged Horses wi
Occupation
Electrical Contractor, Electrical Engineer
It is electrical, not a plumbing fitting, as the threads are not tapered. ;)

Unless you were standing in Britain when you saw it. They have BSPP, British Standard Parallel Threads and seal with an o-ring.

Of course it may have been carried in the plumbing section of the store for use as a threaded sleeve for a concrete or metal wall.

Locknuts and bushings and it would have looked just fine. As is, NO.
 