Can 4" flexible conduit exceed 6' per NEC

Status
Not open for further replies.

Mitchum

Member
Location
California
Occupation
electrical inspector
Can 4" flexible conduit exceed 6' if properly secured? It's a feed to a generator. .................................................................................................................................................
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I suggest you take a look at the article that describes the specific type of flexible conduit you are asking about, but as far as I can recall, there is no length restriction on any of them.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Any flexible raceway of any size used to provide flexibility after installation (like a generator) requires a wire type EGC. As Bob and Larry stated there is no length limit.
 

quantum

Senior Member
Location
LA
Can 4" flexible conduit exceed 6' if properly secured? It's a feed to a generator. .................................................................................................................................................
Since you are asking here, I'm assuming you are installing in a hazardous area? If you are in a class I area, LFMC (etc.) is commonly restricted to a maximum of 6ft in length to comply with 501.30(B)(Exception) (and a few other items). If you have an equipment bonding jumper, however, I don't believe there would be a maximum of 6ft.
 