Why would 392.60(C) refer to 250.102 and not 250.122 when sizing bonding jumpers ????????????????????????????????????????????/
 

Natfuelbilll

Senior Member
It does not seem like it matters much since 250.102(D) refers you to 250.122 fro equipment bonding jumpers.

If it doesn't matter much then why, as this post is asking, does 392.60 (C) point to 250.102? Maybe 392.60(C) should just come out and tell ya to go to 250.122.

o_O
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Why would 392.60(C) refer to 250.102 and not 250.122 when sizing bonding jumpers ????????????????????????????????????????????/
It is possible that the installation would require a supply side bonding jumper and not an EGC. The reference to 250.102 covers both cases.
 