Why would 392.60(C) refer to 250.102 and not 250.122 when sizing bonding jumpers ????????????????????????????????????????????/
If it doesn't matter much then why, as this post is asking, does 392.60 (C) point to 250.102? Maybe 392.60(C) should just come out and tell ya to go to 250.122.It does not seem like it matters much since 250.102(D) refers you to 250.122 fro equipment bonding jumpers.
It is possible that the installation would require a supply side bonding jumper and not an EGC. The reference to 250.102 covers both cases.Why would 392.60(C) refer to 250.102 and not 250.122 when sizing bonding jumpers ????????????????????????????????????????????/
Can a ssbj be anything other than a wire type conductor?It is possible that the installation would require a supply side bonding jumper and not an EGC. The reference to 250.102 covers both cases.
Yes, it can be a non-flexible metal raceway. That does not include cable tray, but it is is often used as such.Can a ssbj be anything other than a wire type conductor?