In CEC (Canadian Electrical Code) book, 8-106(1) says: The size of conductors and switches computed in accordance with this section shall be the minimum used except that, if the next smaller standard size in common use has an ampacity not more than 5% less than this minimum, the smaller size conductor shall be permitted. Does NEC have the similar/same code?
My calculation of the cable size is 551A. The allowable ampacity of 750MCM (90 degree C) is 535A on Table 310.16. Can I use this 750MCM cable or shall I use the next larger cable in common use 1000MCM?