Is it permitted to run conduit between two busway disconnects. Than feed to one common conduit run to feed two 3 phase motor circuits.

Thanks

rmonroe
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: busway

Yes, if there is the space required by 312.8 you can use one of these as a raceway.

Take a look at 312.8 (2002) just make sure you read the whole thing, the first sentence says no, the rest says yes. ;)

I have not found busway switches to have enough room to work the conductors that have to be in there, I would plan on running both to a common J-Box and go from there out to the loads.

Don't forget about derating the conductors 80% as you will have six current carrying conductors in one raceway.
 

tshea

Senior Member
Location
Wisconsin
Re: busway

You can do it for all the reasons Bob gave, but in the greater scheme of things it is not prefered.
1. It looks bad-my opinion.
2. It is potentially dangerous.
3. The next contractor in will be suspicious of the rest of the work in the plant. I know I would!
 